sTemmerman Aug 1, 2023 12:11 PM

Hi,

I'm polling 2 CR1000 logger trough RS232 with an Xbee. 

I was using the terminal commands to poll the VARS (command 7) but sometimes there was an error in the communication.

I found that using  VARS w/o names (command f) is more stable for my application.

The problem is that one of the CR1000 units returns the vars without problem but the other only returns the following.

CR1000>

CR1000>F


CR1000>

CR1000>

CR1000>

But when polling the VARS with names it returns the values.

Is there a setting that needs to be turned on?

Thanks in advance.

Kind regards.


JDavis Aug 1, 2023 03:48 PM

I suspect that CR1000 has an older OS version on it. You should try OS 32.05 on it.