Reset in factory default a cr1000


Benjamin.vial Jan 22, 2025 03:10 PM

Hi,

I picked up an old CR1000 forgotten in the field, and after changing its lithium battery, I realize that there is a pakbus encryption and a tcp password. I don't know it, and I'm pretty sure the guy who does is gone, so I'd like to reset everything to factory settings, so I'll be able to reinstall this datalogger somewhere on another field installation.

Bye


jtrauntvein Jan 22, 2025 08:05 PM

The easiest way to get the datalogger to factory settings from that state is to use the Send OS panel (the onbe shown before you hist the connect button).  This panel uses a different low level protocol that is not affected by pakbus encryption or other datalogger settings (with the exception of RS232 baud rate).