Some one know why the data storage in a CR200X from a TE525MM some times have many decimals?? in example normal records are:
1.2 mm
2.4 mm
0.6 mm
but some times the records are in this way:
0.8000001
4.399998
3.099999
What you think is the reason of this measurements and how i can fix this?
Thank you in advance
This is due to the fact the CR200X logger does its math in single precision floating point arithmetic and also stores data in the same format.
A consequence of this is that even the addition of non-integer numbers are subject to very small internal conversion and rounding errors (this applies to any device working in IEEE4 math).
A simple option in this case is to totalise the number of tips, and store that value, which generally will not result in so many rounding errors.
Alternatively you could just round the floating point numbers post data collection.
Thank you Andrew,
Possible in the program of the CR200X in this case in the data table the totalize instructiona have data type IEEE4?
If i change the data type for FP2 this can help? (or other format of data type)
Thank you
Best Regars
Unfortunately the CR200X only supports IEEE4 data storage (there are no options). In our more advanced loggers (CR800 up) you can select FP2 or integer data format for storage. When you do this the numbers are automatically rounded during the conversion to the alternate format for storage.
Ok
Understud
Thank you very much
Best Regars
I solved this problem with
Public Rain, RainDay
PulseCount (Rain,P_SW,2,0,0.2,0)
RainDay=RainDay+Rain
If FRAC(RainDay)<>0 Then'If the fractional part is not zero
RainDay=RainDay*1000'Give me big number to play with
RainDay=0-RainDay'make it negative
RainDay=FIX(RainDay)'make it the next integer away from zero
RainDay=ABS(RainDay)'make it positive
RainDay=RainDay/1000'make it small again
EndIf
Seems to be working so far