Short distance cable for PakBus between two loggers


TommyC May 29, 2015 01:51 PM

Question: Is it possible to connect to loggers (CR3000) together using a short cable (10') via the CSIO ports?? All of the comm ports are busy for this application. This PakBus network will need to commuticate thru one of the loggers via a Raven cell modem.

Thanks,

Tommy
US Army Corps of Engineers


JDavis May 29, 2015 06:39 PM

You cannot directly connect CSIO to CSIO. Both dataloggers are CSIO master devices. Two SC105 would do the job for a cable short distance. The SC105 does not provide electrical isolation. So, if the dataloggers are not connected to the same power ground, the MD485 is recommended.


TommyC May 29, 2015 06:50 PM

Thanks. Would two NL115's work and a crossover cable? Need both loggers on the Pakbus network with one logger connected to the Raven.

Thanks


Sam Jun 14, 2015 07:21 AM

Yes. You can connect the loggers together over Ethernet.