cr1000 multiple(more than 2) pulse sensors ?


mortenx Jun 3, 2015 07:33 PM

is it possible to connect with cr1000 more than 2 pulse sensors (tiping bucket) ?


Uri Jun 4, 2015 11:22 AM

All Com ports (C1-C8) can do pulse counting.


mortenx Jun 6, 2015 05:58 PM

is it possible to get some sample programs ?


Uri Jun 7, 2015 02:24 AM

It is very easy to create a program with 'Short Cut'. You can add the sensors you wish to connect to your CR1000 and also see the wiring diagram that should follow your setup.
If you already worked with 'CRBasic Editor' just add a 'PulseCount' instruction and use C1 Through C8 instead of P1 or P2 (11-18 in the PChan paramter in the instruction).

This is what a simple 3 tipping buckets program looks like:

'CR1000
'Created by Short Cut (3.1)

'Declare Variables and Units
Public BattV
Public PTemp_C
Public Rain_mm
Public Rain_mm_2
Public Rain_mm_3

Units BattV=Volts
Units PTemp_C=Deg C
Units Rain_mm=mm
Units Rain_mm_2=mm
Units Rain_mm_3=mm

'Define Data Tables
DataTable(Rain,True,-1)
DataInterval(0,10,Min,10)
Minimum(1,BattV,FP2,False,False)
Average(1,PTemp_C,FP2,False)
Totalize(1,Rain_mm,FP2,False)
Totalize(1,Rain_mm_2,FP2,False)
Totalize(1,Rain_mm_3,FP2,False)
EndTable

'Main Program
BeginProg
'Main Scan
Scan(10,Sec,1,0)
'Default Datalogger Battery Voltage measurement 'BattV'
Battery(BattV)
'Default Wiring Panel Temperature measurement 'PTemp_C'
PanelTemp(PTemp_C,_50Hz)
'Generic Tipping Bucket Rain Gauge measurement 'Rain_mm'
PulseCount(Rain_mm,1,1,2,0,0,0)
'Generic Tipping Bucket Rain Gauge measurement 'Rain_mm_2'
PulseCount(Rain_mm_2,1,2,2,0,0,0)
'Generic Tipping Bucket Rain Gauge measurement 'Rain_mm_3'
PulseCount(Rain_mm_3,1,11,2,0,0,0)
'Call Data Tables and Store Data
CallTable Rain
NextScan
EndProg


mortenx Jun 8, 2015 10:26 PM

pulse port P2 is working but control port C1(11) do not count , what seems to be the problem ?

'CR1000
'Created by Short Cut (3.1)

'Declare Variables and Units
Public BattV
Public PTemp_C
Public Pulse
Public Pulse_2

Units BattV=Volts
Units PTemp_C=Deg C
Units Pulse=Counts/Hz
Units Pulse_2=Counts/Hz

'Define Data Tables
DataTable(Table2,True,-1)
DataInterval(0,1440,Min,10)
Minimum(1,BattV,FP2,False,False)
EndTable

'Main Program
BeginProg
'Main Scan
Scan(5,Sec,1,0)
'Default Datalogger Battery Voltage measurement 'BattV'
Battery(BattV)
'Default Wiring Panel Temperature measurement 'PTemp_C'
PanelTemp(PTemp_C,_50Hz)
'Generic Pulse measurement 'Pulse'
PulseCount(Pulse,1,11,2,0,1,0)
'Generic Pulse measurement 'Pulse_2'
PulseCount(Pulse_2,1,2,2,0,1,0)
'Call Data Tables and Store Data
CallTable Table2
NextScan
EndProg


mortenx Jun 10, 2015 09:57 PM

mistake was that control port count`s voltage not ground..


mortenx Jun 10, 2015 09:57 PM

mistake was that control port count`s voltage not ground..