Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

Shortcut CR10X Store time


drCarbon Oct 20, 2015 02:02 AM

I'm using Shortcut to connect to a CR10X. The Store Time appears to be limited to once a minute. Is there a way to store data by the seconds?


jra Oct 20, 2015 01:13 PM

With ShortCut and the CR10X your choices are limited. You can store data at the scan interval (you set that in the first ShortCut screen). When you are on the Outputs screen, step 4, select Advanced Outputs in the lower left corner. Now additional "Store based on:" options appear. Un-check the box in front to Time, check the box in front of "Flags" keep Flag 1 and Low.

Also, you'll want to select Sample as your output type.

Your other option is to load a PakBus Operating System https://www.campbellsci.com/19_1_9999_91 into your CR10X and write the program in ShortCut for a CR10XTD/PB.

Either way, remember that the CR10X has a limited amount of memory. You will need to collect data frequently if it is storing on a fast interval.

I hope that helps.


drCarbon Oct 23, 2015 03:36 AM

thank you. I load the PakBus OS and it seems to work fine.

Log in or register to post/reply in the forum.